BBS Book
BBS Book
Price -490/-
Basic of Bar Bending Schedule Part -1
What is meant by Bar Bending Schedule (BBS)
General guidelines to be followed in preparing BBS
Advantages of Bar Bending Schedule
Steel bar for Rcc Work
General precautions for steel bars in reinforcement
Why Steel is Used in Concrete
What is Tmt Bar and Features of Tmt Bars
Frequently ask question about TMT bar by Interviewer
Overlap Length / Lap Length of Reinforcement in detail.
Why over Lapping of steel is important?/Overlap Restriction
Overlapping of Steel bar in Different Concrete Mix M15,M20,M25,
What is clear cover in concrete / Clear Cover for different Rcc Structure.
Difference in between Clear cover ,Nominal cover and Effective cover
How much bend deduction we take on turning of reinforced bar at 45/90/135/180 deg°
How much does hook length take in a Ring .
BBS is used in finding cutting length of steel and total weight of steel per unit area. and we
can make the bar bending schedule in Ms office Excel software
Hence in order to avoid failure of plain concrete it should be provided with tensile strength.
This is possible by inducing rebars into plain concrete. Hence, it is reinforced (i.e. embedded)
with rebars. The reinforcement bars transfers load between the concrete and rebar. The direct
stress (tensile/pull or compressive/push) transfer takes place form concrete to rebar interface
by means of bond between them i.e. due to friction
As rebars imparts tensile strength to concrete, metals used for rebars should possess good
tensile strength. This will avoid cracking of concrete in tension. Though there are many
metals like Aluminum, Cast Iron, Copper available for reinforcing concrete, Steel is most
widely used as reinforcing material in reinforced concrete. It is because the two materials
bond together very well with no slippage and thus act together as one unit in resisting the
applied loads, apart from few other important properties of steel.The tensile strength of steel
is approximately equal to 100 – 140 times the tensile strength of plain concrete mix.
What is TMT BAR
TMT bars or Thermo-Mechanically Treated bars are high-Strength Reinforcement
bars having a tough outer core and a soft inner core. The very first step of the
manufacturing process involves passing the steel wires through a rolling mill stand.
Thereafter, these rolled steel wires are again passed through the Tempcore water cooling
system. While passing the wires through the water cooling system, the water pressure is
optimised. The sudden quenching and drastic change in temperature toughen the outer
layer of the steel bar, thus making it super tough and durable. Once this process is over,
the TMT bars are subject to atmospheric cooling. This is done in order to equalise the
temperature difference between the soft inner core and the tough exterior. Once the TMT
bar cools down, it slowly turns into a ferrite-pearlite mass. The inner core remains soft
giving the TMT bar great tensile strength and elongation point.
This design is unique to the TMT bars and gives superior ductility to the bars. Also, this
unique manufacturing technique and the absence of Cold stress make this bar corrosion-
resistant and boost its weld ability
Q: Is TMT Bar used for high rising building, bridges & dams only?
Not at all. It is used for all types of construction works ranging from buildings to
dams.
Overlap Length in
Compression 50D
REBAR
COUPLER
Results of the study reveal that the use of rebar couplers in place of lapping is
considerably cost effective for larger diameter bars such as 32 or 40 mm bars.
Other than the cost, the other obvious advantage of couplers is avoiding
congestion of rebars which may occur at a lap zone,now a day moistly use
coupler in construction.
Why over Lapping of steel is important?
The overlapping of the steel is very important in R.C.C works because splicing of steel is
used to transfer all the stresses from one bar to another bar. The length of the lapping is
different in different concrete mixes because different concrete having a different crushing
strength.
At the site basically, we receive a steel bar at the site having a length 6 to 12 meter. So if we
have a length more then 12 m. We must overlap the steel bar so the splice length of the steel
bar depends on the,
Suppose we have a column having a height 100 ft. So at the side, we don’t have a 100 ft long
one single bar we must overlap the bar to achieve the total length of the column.
OVERLAPPING RESTRICTION
1. The lapping is not provided above 36 mm diameter bars because those diameter bars
doesn’t transfer the stresses from one bar to another bar and also the alignment of the
column bar is also affected by providing the lap on these bars.
2. The lapping of the steel bars also not provided in high shear force zones and it should be
provided at that zone where shear force will be minimum.
OVERLAPPING OF STEEL BARS IN DIFFERENT
CONCRETE MIX
Basically, we have three types of zone Compression zone Neutral zone and Tension zone. In
different zones, we provide different splice length of the steel bars. In R.C.C construction we
mainly use 3 types of concrete mix M15, M20, and M25.
M 15 CONCRETE MIX
In M 15 we use the concrete mix 1 : 2: 4 means 1 part of cement, 2 part of sand and 4 part of
aggregates.
Tension zone develops at the bottom of the Beam, Slab etc and the compression zone
developed at the top. In the tension zone, steel bars resist against elongation etc.
M 20 CONCRETE MIX
In M 20 we use the concrete mix 1: 1.5 : 3 means 1 part of cement, 1.5 part of sand and 3 part
of aggregates.
Tension zone Compression Zone.
Fe 250 – 46 ∅ Fe 250 – 37 ∅
Fe 415 – 47 ∅ Fe 415 – 38 ∅
Fe 500 – 57 ∅ Fe 500 – 46 ∅
M 25 CONCRETE MIX
In M 25 we use the concrete mix 1 : 1: 2 means 1 part of cement, 1 part of sand and 2 part of
aggregates.
Tension zone Compression Zone.
Fe 250 – 39 ∅ Fe 250 – 32 ∅
Fe 415 – 41 ∅ Fe 415 – 33 ∅
Fe 500 – 49 ∅ Fe 500 – 39 ∅
Where ∅ is the diameter of the bar. Suppose we are using a steel bar Fe 500 and concert mix
M25. The diameter of the bar will be 12 mm. By using the formula, the splice length of the
steel bar will be 49 x 12 = 588 mm and if the bar is in tension zone and 39 x 12 = 468 mm if
the bar is in the compression zone.
Note: These all formulas are commonly used at the site but also concern your site engineer
before going to use these formulas.
What is clear cover in concrete
The Clear Cover Is the Distance measured From the Exposed concrete Surface ( without
Plaster And Other Finishes) to the nearest Surfacae of reinforced bar.
They were made up of 1:3 ratio of cement mortar. Cover blocks should be immersed in water
for 14 days to get the maximum strength.All the beams,column, slab,were checked to ensure
adequate cover blocks are provided to the bottom and sides of the reinforcement. Main bars
of the columns were adjusted to ensure the covering requirements before concreting. Chair
of correct height were used to maintain the require gap between top and bottom
reinforcement nets and cover blocks were also provided to bottom reinforcement
1. Clear cover: This is the distance from the face of the member to the outermost face
of the reinforcement including shear or torsion Stirrups or links.
2. Nominal cover: This is the same thing as clear cover albeit with a different name.
This term is used by the code. It is the distance measured from the face of the
member to the outermost face of the reinforcement including Stirrups or links. It is
the dimension shown in drawings and detailing.
3. Effective cover: This is the distance measured from the face of the member to the
center of area of the main reinforcement, that is tension or compression
reinforcement. This is the dimension usually used for design calculations
Cover Cover
How much bend deduction we take on turning of
reinforced bar at 45° 90° 135° & 180°
Remember,
HOOK 9d to
12d
Bar Bending Schedule
Part - 2
Diameter of Reinforcement Bar Easily Available
Steel bars does not vary according to the structure. They vary according to loading
conditions imposed on the structure.Whatever the structure it is Footing, Raft,
Columns, Beam and Slab The most commonly used bars and available in shelf at all
times are 6mm, 8mm, 10mm,12mm,16mm,20mm,25mm are available easily outside
also. In most of the buildings we use max 25mm. only in some places 32mm also
available. greater dia like 64mm and 128mm has to be ordered specially from steel
plant for manufacturing unit.
Standard Length of the Steel Bar Standard Length of the Steel Bar
In Meter(MKS) In Feet(FPS)
(Bars are sold at standard Length) (Bars are sold at standard Length)
12M OR 12.19M 39’4” or 40’
Formula to Find Weight of Formula to Find Weight of
Bar in Meter Bar in Feet
Moistly we Calculate in all process in MKS System because More Accuracy is found in
the MkS System..
2.1 Procedure To Find Cut Length Of Main Bar or
Distribution Bar in mesh
Breadth 5mtr
10 mtr
Civil Engineer Fieldwork Expert BBS
Length of hook =9d where d is the diameter of bar.if both side Providing then
Total Length of Distribution Bar = L+9d(one side)+9d(another side)-(2 90°bend)
Now for example. Dia of bar "d”=12mm
So 9d=9x12=108mm we Convert into Meter (108/1000)=.108 mtr
For bend ( 2 x 2 x d) = (2 No. x 2 x 12) = 48mm = (48/1000) = .048 mtr
Total Length of Distribution Bar = 10+(9d)+(9d)-bend
= 10+.108+.108 - .048 = 10.168 mtr
Cutting Length Of Main Bar With Bend : if Bend Providing Both Side
(9d to 16d)
L=5mtr
Length Of Bend = 9 d to 16 d
Where d is the Diameter of bar.
Total Length of Main Bar = L+10d+10d –(2 x 2d)
Now For Example, d= 16mm then
So 10d = 10x 12=120mm We convert into meter (120/1000)=.120 mtr
For bend ( 2 x 2 x d) = (2 No. x 2 x 16) = 64mm = (48/1000) = .064 mtr
Total Length of Main Bar = 5 + .120 + .120 - .064
= 5.176 mtr
Civil Engineer Fieldwork Expert BBS
10000
+ 1
= 100
10000
= + 1
100
= 100 + 1 = 101 Nos.
Note – In this Calculation We learn only how to find cut length of main or dist bar in
mesh and How to find number of main bar or dist.bar without Clear Cover
2.2 Procedure to find out cut length of “2L” Rectangular
Stirrups
Suppose we have a beam having a Width 230 mm and having a Depth 450 mm.The
diameter of the stirrup bar is 10 mm. The clear cover in the beam is 35 mm.
10mm-2No.
Ring 150mm c/c
Ring 10mm@150c/c
16mm-3 No.
450mm
Step 1: Mark c/c distance of stirrup along base as ‘a’ as per the given structural
drawing of stirrup.
Step 2: Mark c/c distance of stirrup along depth stirrup as ‘b’ as per the given
structural drawing of stirrup.
Step 3: Calculate a & b separately from the given structural drawing of stirrup.
Step 4: See hook Detail in DWG and Count No.of bend for 90degree or 135degree.
Ring 10mm@150c/c
16mm-3 No.
b 450mm
230mm
= 150 mm
= 370 mm
By putting the given values in the formula we get the length of the stirrup.
Length of the bar = 2(150 + 370) + 2(10 x 10) – 3(2 x 10) – 2(3 x 10)
= 1040 + 200 – 60 – 60
= 1040 – 120
= 1120 mm or 1.120 m.
2.3 Procedure to find out cut length of “4L” Rectangular
Stirrups
Suppose we have a Beam having a Depth 500 mm and having a Width 400mm.
The diameter of the stirrup bar is 8 mm. The clear cover in the Column is 30 mm
4T20mm
400mm
GIVEN DATA:
Step 1: Mark c/c distance of stirrup 1 along width base as ‘a’ as per the given
structural drawing of stirrup.
Step 2: Mark c/c distance of stirrup 1 along depth side as ‘b’ as per the given
structural drawing of stirrup.
Step 3: Calculate a & b separately from the given structural drawing of stirrup.
Step 4: See hook Detail in DWG and Count No.of bend for 90degree or 135degree.
Step 5: Now, calculate the cutting length of stirrup 1.
Step 6: We know that Cutting Length of Stirrup 2 is same as stirrups 1. Bcoz 4Legged
First Caculate Ring No. 1
4T20mm
400mm
Note - Cutting Length of Ring 2 = same as ring 1 bcoz size of ring is same.
2.4 Procedure to find out cut length of Helix (Spiral) Cage.
600mm
Given
Diameter of Column = 600 mm
Height of Column = 10 m
Clear Cover = 40 mm
Spacing in Spiral = 100 mm
Dia. of Spiral Stirrup = 8mm
= 1632 mm
= 1.632 m
Civil Engineer Fieldwork Expert BBS
Length of Column
No of Spiral = + 1
Pitch or Spacing
= 10000 =+ 1
100
= 101
Total Cutting Length Of Spiral Case = No. Of Spiral x Length of one Spiral
= 164.832 m
2.5 Procedure to find out cut length of Trapazium Shape
Stirrups
If we have col. 400 x 600 mm ..in this Column we found trapezium stirrups ,,,
Now,What is the procedure of Calculating This Stirrups.
600mm
All Main Dia 20mm
Given
d c
a
Centre to centre distance
= {(Length of Column) – (2 x Clear Cover) – (2 x Stirrups Dia) – (2 x Half of Main Vertical Bar Dia)} /
d c
a
Centre to centre distance
Calculation of b = (C/C distance of Main Vertical Bar) + (2 x Half of Main Vertical Bar Dia)
+ (2 x Stirrups Dia)
= 161 + (2 x 10) + (2 x 8)
= 161 + 20 + 16
= 197 mm
Civil Engineer Fieldwork Expert BBS
BASE = C/C Dist. of Main Bar + (Half of Main Bar Dia) + (Stirrups dia)
161
= 161 + 10 + 8 = 179 mm
Calculation of c = { (BASE)^2 + (HEIGHT)^2} By Pythagoras Theorem..
= √ { (179)^2 + (320)^2}
= √ (32041 + 102400)
= 367 mm
d c
a
Centre to centre distance
Civil Engineer Fieldwork Expert BBS
= 1491 mm
2.6 Procedure to find out cut length of Traingular Shape
Stirrups
Procedure to be followed for calculating cutting length of Traingular stirrup:
Step 1: Mark c/c distance of stirrup along base as ‘a’ as per the given structural
drawing of stirrup.
Step 2: Mark c/c distance of stirrup along side of triangular stirrup as ‘b’ as per the
given structural drawing of stirrup.
Step 3: Calculate a & b separately from the given structural drawing of stirrup.
Step 4: To calculate H from the given stirrup drawing, draw a perpendicular from
apex of triangular stirrup to base of stirrup which is equal to ‘b’. (Refer Figure - 2)
2 bend135°
135
H H (485mm)
b
1 bend135° 1 bend135°
a/2 a/2
512 mm
H = √((a/2)² + b²)
H = √((a/2)² + b²) = √((512/2)² + (412)²)
H = 485mm.
Now, Cutting length of Traingular stirrup
= 2 x H + a + hook – bend (135˚)
= 2 x H + a +(2x10xd) – (4no. X 3 x d)
= 2 X 485 + 512 +(2 X10X8) – (4X3X8)
= 1546mm = 1.546m.
2.7 Procedure to find out cut length of Diamond Shape
Stirrups
Stirrups: Stirrups are lateral ties provided in column to resist shear force and to hold
longitudinal bars (main bars) of column in position.
Step 2: Calculate any one side of rhombus, H using hypotenuse formula. (refer
Figure - 2)
Calculation part:
600mm
500mm
a/2
b/2 500mm
b/2
H
a
Civil Engineer Fieldwork Expert BBS
H = √((a/2)² +( b/2)²)
= 1400.84mm = 1.4m
2.8 Procedure to find out cut length of Circular Column
Stirrups
Example...if we have circular column size 600 mm....then how to find Cutting
Length
600 mm
d =(600-40-40-4-4)
Civil Engineer Fieldwork Expert BBS
Given....
d= (Total Diameter of column – both side cover – both side stirrup half dia.)
For small area of construction, you can hand over the reinforcement detailing to the
bar benders. They will take care of cutting length. But beware, that must not be
accurate. Because they do not give importance to the bends and cranks. They may
give some extra inches to the bars for the bends which are totally wrong. So it is
always recommended that as a site engineer calculate the cutting length yourself..
Where,
Diameter of the bar = 12 mm
Clear Cover = 25 mm
Clear Span (L) = 8000
Slab Thickness = 200 mm
Development Length(Ld) = 40d
Cutting Length = Clear Span of Slab + (2 x Development Length) +
(2 x inclined length) – (45° bend x 4) – (90° bend x 2)
Slab thick.200mm
90° bend 1 d
Ld
Span 8000mm
Column Column
Civil Engineer Fieldwork Expert BBS
Cutting Length = Clear Span of Slab + (2 X Ld) +(2 x 0.42D) – (1d x 4) - (2d x 2)
Slab thick.200mm
Ld
Span 8000mm
Cutting Length = Clear Span of Slab + (2 X Ld) +(2 x 0.42D) – (1d x 4) – (2d x 2)
[BBS Shape Codes]
Where,
d = Diameter of the bar.
Ld = Development length of bar.
D = Height of the bend bar.
In the above formula, all values are known except ‘D’.
So we need to find out the value of “D”.
D = Slab Thickness – (2 x clear cover) – (diameter of bar)
= 200 – (2 × 25) – 12
= 138 mm
Given :-
Raft Footing
Height of footing = 1.2 m
Main bars & dist. Bar = 16 mm dia @150 mm c/c Top or Bottom.
Clear Cover = 50 mm
Cutting length of chair bar = ?
Chair Height =Footing Height - [(Upper + Lower Side Cover) + (Upper side main & dist. bar dia +
lower side main bar dia)]
Step 3 : Chair bar leg = 2 nos c/c distance + 50 mm (bars which are located at bottom)
= 2 x 150 mm + 50 mm = 350 mm
Length
2000 mm
Width
1500 mm
C1
PCC
Dist.Bar 10mm@150c/c
Main Bar 12mm@100mm c/c
Distribution Bar
Main Bar
Shape Of Main Bar Distribution Bar
Main Bar
2000 mm
1500 mm
= 1500 – (2 x 50)
+ 1
150
= 1400 + 1
150
Length
3000 mm
Width
2000 mm
450 mm C1
PCC
Dist.Bar 8mm@150c/c
Main Bar 10mm@100mm c/c
Distribution Bar
Given Main
MainBarBa
Size of Footing(CF2) = 3000mm x 2000mm
Civil Engineer Fieldwork Expert BBS
Height = 450mm
Clear Cover = 50 mm
No. Of Footing = 2 nos
Main Bar Top or Bottom = 10mm @ 100 mm c/c Spacing
Distribution Bar Top or Bottom = 8mm @ 150 mm c/c Spacing
50 3000mm 50
3000 mm
2000 mm
= 60 Nos.
Step : 4 Number of Top or Bottom Distribution Bar(10 mm ) in Footing.
Distribution Bar
Number of Main Bar = width – (2 x Clear Cover) + 1 8mm@150mmc/c
Spacing
Main Bar
2000 – (2 x 50) + 1
= 150
1900
= + 1
150
= 13.66 Nos{14 bar}. X 2(top or bottom)
= 28 Nos.
Zone A
Slab 125mm
300mm
Zone A
Cutting Length of Vertical bar 20 mm= (Length of bar Below Plinth Beam)+(Plinth Beam)
+ (Full Length of Bar Above Plinth beam)
Cutting Length of Vertical bar 20 mm= (Length of bar Below Plinth Beam)+(Plinth Beam)
+ (Full Length of Bar Above Plinth beam)
Civil Engineer Fieldwork Expert BBS
= 1860 mm + 300 mm + 13375 mm
15.335m > 12m i.e. provide Overlap According to Practically Requirment...if we will provide
1 lap only then..problem face in handling of vertical bar,so Overlap Provide Floor to Floor
For Easily Handling and Perfection in Alignment of bar..
= 15535 + ( 4 x 50 x d)
= 15535 + ( 4 x 50 x 20)
= 15535 + 4000
OverLap Note Point – 1.Splice Located minimum but away from column & Beam
Junction.this portion left Atleast L/4 portion ,
2.Laps should be staggered and alternate.
3.Laps should not be parallel to each other.
Step 2 – Find the Cutting length of Vertical Bar(16mm)
First we Calculate Ful Length Of Bar below Plinth Level
Length of bar Below Plinth Beam
= (Column L) + (Footing Height – Clear Cover – Main bar – Dist.Bar) + (Column Height below Plinth)
= 300 + ( 450 – 50 – 20 – 20 ) + 1200 mm
= 300 + 360 + 1200 mm
= 1860 mm = 1.860 Meter
Cutting Length of Vertical bar 16 mm= (Length of bar Below Plinth Beam)+(Plinth Beam)
+ (Full Length of Bar Above Plinth beam)
= 15335 + ( 4 x 50 x d)
= 15335 + ( 4 x 50 x 16)
= 15335 + 3200
Cutting Length of Vertical bar 16 mm= 18535 mm or 18535 Meter
Ld 800mm
Slab 125mm 1st Number of Ring in Zone A ????
L/4 Zone A 750
Number of Ring =( Distance/Spacing)+1
3000mm
L/2 Zone B 1500
Zone A Total Length
= 1650 + ( 8 x 750 ) + (3x125 Slab )+(300 beam)
L/4 Zone A 750
Zone A 750
Slab 125mm
Spacing
Zone A 750 2nd Number of Ring in Zone B ????
100mm
Ld
20mm 4 nos
16mm 2 nos
Column L 300mm
Development Length Ld 50 d
Hook 9d
Number of Column 10
Step 1 – Find the Cutting length of Vertical Bar(20mm)
Cutting Length of Vertical bar 20 mm= (Length of bar Below Plinth Beam)+(Plinth Beam)
+ (Full Length of Bar Above Plinth beam)
Cutting Length of Vertical bar 20 mm= (Length of bar Below Plinth Beam)+(Plinth Beam)
+ (Full Length of Bar Above Plinth beam)
= 1860 mm + 300 mm + 4000 mm
Second we Calculate Ful Length Of Bar Above Plinth Level. Civil Engineer Fieldwork Expert BBS
= (G.F Height + Slab Ld)
={ 3000 + (50 x 16)}
= 3000 mm + 800 mm
=3800mm=3.8 Meter.
Cutting Length of Vertical bar 16 mm= (Length of bar Below Plinth Beam)+(Plinth Beam)
+ (Full Length of Bar Above Plinth beam)
Ring 8mm@150c/c
PB1 PB1 12mm-2No.
230mm
PB1 PB1
No of PB2 BEAM =2
Step 1 : Find cutting length of Main top bar
Ld
Column Column
Cutting length of top bar = Clear Span + 2 x Development length( Ld ) – (2 bend 90deg)
= 5760 mm
Ld
Bottom bar 16mm 3 no.
Column Column
Cutting length of Bottom bar = Clear Span + 2 x Development length( Ld ) – (2 bend 90deg)
= 6216 mm
Step 3 : Find Out No. Of Ring in Beam.
= 1176 mm
See BBS For Plinth Beam
In pdf Sheet - 5
3.6 Bar Banding Schedule For Beam With Extra Bar
Suppose Same Drawing Span Related to Plinth Beam Drawing,then how to find BBS
1250mm
Top Extra 2nos 16mm 1250 mm
A
L/4 L/4
L/6 L/6
A Bottom Extra 2nos 20mm
833mm 833mm
5000mm (B2 Beam)
A
Bottom Main 3nos 16 mm
16mm-2No.
Spacing Detail
L/6 L/6
Ld
Span 5000mm B2
Column Column
Cutting length of top bar = Clear Span + 2 x Development length( Ld ) – (2 bend 90deg)
450 B2
16mm-3 No.
230mm
Column Column
Civil Engineer Fieldwork Expert BBS
Cutting length of Bottom bar = Clear Span + 2 x Development length( Ld ) – (2 bend 90deg)
= 6216 mm
Step 3 : Find cutting length of Main top Extra bar
1250mm
Top Extra 2nos 16mm 1250 mm
L/4 L/4
L/6 L/6
Bottom Extra 2nos 20mm
833mm 833mm
5000mm (B2 Beam)
Civil Engineer Fieldwork Expert BBS
Cutting length of top Extra bar = L/4 Span + Development length( Ld ) – (1 bend 90deg)
= 1858 mm
Cutting length of top Extra bar = Total Span – L/6 Span Both Side
= 5000 – (2 x 5000/6)
= 5000 – (2 x 833)
=5000 – 1666
= 3334 mm
Step 3 : Find Out No. Of Ring in Beam.
Spacing Detail
8mm Ring
230mm
B
Length of One Hook = 9d
Calculation of A = 450 – 25 – 25 – 4 – 4 = 392
Calculation of B = 230 – 25 – 25 – 4 – 4 = 172
Cutting length of Stirrup = Perimeter of stirrup + No. Of Hook – Bend Deduction90/135deg
= 2(A+B) + (2x9d Hook)-(3x2d 90Deg Bend)-(2x3d 135 Deg Bend)
= 2(392+172) + ( 2x9x8) - (3x2x8 ) - (2x3x8)
= 1176 mm
See BBS For Beam with Extra
In pdf Sheet -6
3.7 BAR BENDING SCHEDULE OF LINTEL BEAM
2 nos 12mm
2500 mm 230mm Ø
150mm
Given
Length of Lintel (L1) = 2500 mm
Clear Cover = 25 mm
Dimension of Lintel = 230 x 150mm
Stirrups = 8mm Ø @ 125 c/c
Top Reinforcement = 12 mm Ø 2 nos
Bottom Reinforcement = 16 mm Ø 3 nos
Number Of L1 Lintel = 10
Length of Top bar = Length of lintel – clear cover for both sides
= 2500 – 2 x 25 [Clear cover for both sides]
=2450 mm
= 2.4 m.
Length of Bottom bar = Length of lintel – clear cover for both sides
= 2500 – 2 x 25 [Clear cover for both sides]
= 2450 mm = 2.4 m
Step 3. Cutting Length Of Stirrups:
Civil Engineer Fieldwork Expert BBS
a = 230 -25 -25 -8 = 172 mm
b = 150 – 25 – 25 -8 = 84 mm.
Cutting length of stirrups = 2(a+b) + Hooks Length – Bend
Hooks length = 10d
230mm
Step 4. Calculate No Of Stirrups:
b 150mm
3800mm
300
c/c
1800mm
500mm
Pcc
100mm 750mm 600mm 1650mm 100mm
Given
Length of Retaining Wall = 30 m Civil Engineer Fieldwork Expert BBS
Clear Cover in Footing = 50mm
Clear Cover in Stem = 30mm
Base Slab Reinforcement
Main Bar @ 20mm @ 150mm c/c(top or bottom)
Dist. Bar @ 12mm @ 250mm c/c(top or bottom)
Stem Reinforcement Left Side
Main Bar @ 12mm @ 200mm c/c
Dist. Bar @ 8mm @ 250mm c/c
Stem Reinforcement Left Side
Main Bar @ 16mm @ 300mm c/c(low/medium/high)
Dist. Bar @ 8mm @ 300mm c/c(full Height)
Step 1 : Find Cutting Length of Main/Dist. Bar of Base Slab
500mm
250mm
Pcc
750mm 600mm 1650mm
Cutting Length of Main Bar = Total width of Footing – Clear Cover + “L” Length - Bend Deduction
= (750+600+1650) – (2 x 50) + ( 2 x 250) – (2 x 2d 90 deg bend)
= 3000 mm - 100mm + 500 mm – ( 2 x 2 x 20)
= 3000 mm - 100mm + 500 mm – 80 mm
= 3320 mm = 3.320 m
Cutting Length of Dist. Bar = Length of Footing(30m) – Clear Cover + “L” Length -
Bend Deduction + Overlap50d
= (30000) – (2 x 50) + ( 2 x 250) – (2 x 2d 90 deg bend) + (2 x 50 x 12 )
= (30000) – (2 x 50) + ( 2 x 250) – (2 x 2 x 12 ) + (1200)
= 30000 mm – 100 mm + 500 mm – 48 mm + 1200
= 31552 mm = 31.552 m
300mm L 20 mm
500mm
Cutting Length of Main Bar Left Side = Total Height – Clear Cover top + “L” Length - Bend Deduction
= {Stem + Base Slab} – Clear Cover top + “L” Length - Bend Deduction
= { 6000 + (500-cover-main-dist)} – 30mm top cover + 300 – (1 x 2 d)
= { 6000 + (500-50-20-12)} – 30 + 300 – (1 x 2 x 12)
= { 6000 + 418} – 30 + 300 – 24
= 6664 mm = 6.664 m Civil Engineer Fieldwork Expert BBS
Cutting Length of Dist. Bar Left Side = Length of Footing(30m) – Clear Cover + Overlap50d
= (30000) – (2 x 50) + (2 x 50 x 8mm )
= 30000 – 100 + 800
= 30,700 mm = 30.7 m
3800mm
300
c/c
1800mm
300
300mm L
Main Bar 16mm @300
c/c 300
500m
m
Pcc
100 100 100
16 mm Dia main Bar Medium= {Stem + Base Slab} +( “L”Length botm ) - Bend Deduction
= {3800 + 418 } + 300 - (1 x 2 x 16 )
= 4486 mm = 4.486 m
16 mm Dia main Bar Short = {Stem + Base Slab} +( “L”Length botm ) - Bend Deduction
= {1800 + 418 } + 300 - (1 x 2 x 16 )
= 2486 mm = 2.486 m
8 mm Dia Dist Bar Right Side = Length of Footing(30m) – Clear Cover + Overlap50d
= (30000) – (2 x 50) + (2 x 50 x 8mm )
= 30000 – 100 + 800
= 30,700 mm = 30.7 m
No. Of Stem Main Bar Right Side = (Length – Side Cover)/Spacing + 1
= (30000 – 100)/ 100 + 1
= 300 Nos total main bar
= 100 main bar long
= 100 main bar medium
= 100 main bar short
5000mm
Lx span
A 8mm@150c/c
12mm@150c/c
Ld
Cranked
SupportBar Sec A-A
8mm@150mmc/c
B B
L/4
5000mm
12mm@150c/c A 8mm@150c/c
150mm Slab Ld
thickness
Sec B -B
Civil Engineer Fieldwork Expert BBS
Given
Main bars =12 mm @ 150 mm c/c spacing
Distribution bars = 8 mm @ 150 mm c/c spacing.
Cranked support bar = 8mm @ 150 mm c/c spacing.
Top and Bottom. Clear Cover = 25 mm
Development length = 40 d
Slab Thickness = 150 mm
See Slab Section
Bar Bending Schedule Calculation for One Way Slab
Lx=5000
Ly=2000
Ld
12mm@150c/c
L/4 L/4
(Lx)5000m Dist.Bar
m 8mm@150c/c
Ld
Shape of Dist. bar
Step 3..Number of Bar required for Both Side Cranked Support Bar.
Cranked
Support Bar
Ld
8mm@150c/c
L/4 L/4
Lx
A 8mm@150c/c
12mm@150c/c
Ld
Cranked
SupportBar Sec A-A 3000mm
8mm@150mmc/c
B B
L/4
4000mm
150mm Slab Ld
thickness
Sec B -B
Given
Main bars 12 mm @ 150 mm c/c spacing
Distribution bars 8 mm @ 150 mm c/c spacing.
Cranked support bar 8mm/10mm @ 150 mm c/c spacing.
Top and Bottom Clear Cover is 25 mm
Development length 40 d
Slab Thickness – 150 mm
See Slab Section
Bar Bending Schedule Calculation for Two Way Slab
Lx 4000 mm
Ly 3000 mm
Ld
12mm@150c/c
L/4 L/4
Shape of BAR
Lx 4000mm
we know that one side crank inclined length is 0.42D D = Slab thickness – 2 side
clear cover – dia of bar
= 4000 + (2 x 40 x 8) + (1 x 0.42 x D) – (1d x 2) ) – (2d x 2) = 150 – 50 -12 = 88 mm
= 4000 + 320 + (0.42×88) – (1x8x2) ) – (2x8x2)
= 4612mm or 4.61 m
Step 3 Calculate Top Bar (Extra) ; Top Bars are provided at the top of critical
length (L/4) area, Please refer the drawing section A-A
Ld
8mm@150c/c
L/4 Ly 3000 L/4
Ly 3000mm
B B
L/4
Lx 4000mm
150mm Slab Ld
thickness
Sec B -B
Cranked
Support Bar
Ld
Lx 4000mm 12mm@150c/c
L/4 L/4
Now, we will Find The Reinforcement Of OverHead Water Tank Circular Slab
Circular Slab
BBS
Main Bar
12mm@ 200 c/c
Diameter = 2000 mm
1st Half
2nd Half
First of all, you have to calculate the number of rods that means, how many L’s we
need to calculate.
Diameter = 2 x Radius
L5
L3 L4
L1 900
L2 700
500
1st Half
300
Center line of slab 100
200
2000 mm
2nd Half
L1 900 h5
L2 700 h4
500 h3
1st Half
300 h2
Center line of slab 100 h1
200
2000 mm
2nd Half
By Using Pytha goras Theorem ,Calculate Cutting Length of 1st Half Bar L1,L2,L3,L4,L5
Note – We need to calculate the Typical L’s for the 1st half only, for the 2nd half we
will multiply it by 2 excluding the main bar.
And we not need to calculate distribution bar because cutting length of the bar are